apkungen said:
The cell is still good I am sure since it charges up to the same voltage every time even though the bms doesn't work.
<snip>
I have tried leaving it on for maybe 15h, still exactly 3.88V in the cell
Remember, the BMS does not charge the low cells.
The BMS drains the high cells.
Until the high cells drain quite a lot, you won't see much, if any, change in voltage of the low cell, because it is in the middle of the charge curve where it takes a lot of capacity change to make a little voltage change.
Are you measuring the high cells and watching them during the entire charging process? If not you are probably missing that they are charging up to just past full, then the BMS shuts off charging, then drains down that tiny bit of extra charge.
Then if the charger is designed to kick back on once the BMS re-allows charging (many are, but not all), then the current resumes and the process repeats.
As bad a problem as you have there, the process takes much more than 15 hours depending on the balancing current capabilities of the BMS.
BMS are only intended to keep small imbalances at bay, not the kind of problem you have there--those kinds of severe imbalances are meant to be fixed separately, by replacing problematic cells and manually ensuring they are at the same charge state as the other cells, and *then* letting the BMS fix any minor imbalance.
Also, the cell group itself may have at least one damaged cell that is discharging down to that voltage for some internal reason, and shorting all the other cells in parallel with it to the same voltage. You'd have to disconnect the cells in the group from each other to find which one is doing that.
You can also use a single cell charger to bring up the low group at least a little, then watch it with a meter and see if it goes back down again.
so either the bms isn't getting any current at all from the charger after it has gone green or the bms it crap, probably the latter.
If you don't know, then you should measure it. Otherwise you don't know if you are wasting money on something that isn't needed, if the BMS is already doing it's job.
If you have a multimeter, it probably also has an Amps setting. If you put the meter in series with the charger's positive lead (or negative, doesn't matter, just one at a time), with it set to A, you can see how much current flows at any time. Series would be positive meter lead to positive charger lead, and negative meter lead to positive battery lead.
Or use a wattmeter.
Another problem you could have, since there was a physical impact involved, is wires and cells with damaged insulation you may not be able to see. If it's not a complete short, it could be draining that group of cells at a rate slow enough to not completely kill them, but to force them to unbalance.
Also, if you added cells to that group, the added cells could have problems either originally or from the work done to add them (overheating during soldering, for instance).
If you added cells because that group was low in voltage after the impact but not before, then the group probably shorted against something. The short could have damaged the existing cells, especially if they discharged at a high enough rate to internally heat them too much, but not enough to make them catch fire. That kind of internal damage has unpredictable results, and can include being unable to charge past a certain voltage, or being unable to hold a charge above that.
Until you thoroughly test the pack's cells and groups, and wiring (including balancing wires to the BMS) and get them charged evenly, you don't know what part of the pack is actually causing the problem.
Making the assumption that it's the BMS may cause you problems down the line up to and including a fire, if there are damaged cells or wires inside the pack.