Contactor connection pole

artvk

100 mW
Joined
Sep 13, 2017
Messages
45
Location
Bangkok
Hi guy,

I would like to know is it matter about connecting the right pole A1 and A2 in contactor ?
I got Kilovac LEV200. Will contactor destroy if connect wrong pole , I saw A1 and A2 with + - marked on it.
What is happen if connecting wrong side of the pole ?

Thanks
 

Attachments

  • F7823055-01.jpg
    F7823055-01.jpg
    14.5 KB · Views: 679
These contactors have a magnetic blowout. That's an internal magnet to direct or lessen the arc. As such, they are polarity sensitive. The direction of the arc diversion is reversed if the current flows the opposite direction. Reverse polarity may just shorten life or worst case will cause the contacts to weld closed.