Hi all! Bit of a conundrum I can't seem to make ground on...
Due to some unfortunate geometry, I'm going to have to fit my batteries in two banks, about two metres apart. Each bank will have two 200Ah 12v batteries (4 cell LiFePo4). I'll need these to all end up in parallel, for 800Ah at 12V. The max constant discharge will be 300A.
The problem I'm having is how to wire these to achieve that, bearing in mind that all of the electronics (chargers/inverters etc) will be adjacent to one of the banks (and hence 2m from the other bank).
My thinking is thus:
Naming the batteries 1, 2, 3 and 4 (where 1 and 2 are adjacent to the electronics and 3 and 4 are far away), if I take the positive from 1, I should be returning the negative to 4 in an ideal situation. This involves running three 2m cables (to connect 2 and 3 and a negative wire from 4 to the electronics). (Option A)
I could potentially wire them such that 1 connects to 3, 3 to 4, and 4 to 2. This would involve using four 2m cables (two from 1 to 3, two from 4 to 2). This would then allow me to use a short negative cable from 2. (Option B)
The question then, is what these distances/layouts do to voltage drop and wire thickness consideration? To try to ask for some specifics rather than leave it that wide...
1) When considering the 'circuit distance' from battery to inverter (etc) back to battery, what consideration is given to the wiring between batteries/cells in a parallel setup?
2) In Option A, assuming 25cm from Battery 1 to an inverter, and 2m from Battery 4 to the inverter, the total distance is either 2.25m or 4.25m or 6.25m depending on the answer to 1. In Option B, assuming the same 25cm from Battery 1 and 25cm from Battery 2, the total distance is either 0.5m, 4.5m or 8.5m. Which is it?
3) Is there a better way to wire this? :lol:
Many thanks in advance for any help anyone can offer!
Due to some unfortunate geometry, I'm going to have to fit my batteries in two banks, about two metres apart. Each bank will have two 200Ah 12v batteries (4 cell LiFePo4). I'll need these to all end up in parallel, for 800Ah at 12V. The max constant discharge will be 300A.
The problem I'm having is how to wire these to achieve that, bearing in mind that all of the electronics (chargers/inverters etc) will be adjacent to one of the banks (and hence 2m from the other bank).
My thinking is thus:
Naming the batteries 1, 2, 3 and 4 (where 1 and 2 are adjacent to the electronics and 3 and 4 are far away), if I take the positive from 1, I should be returning the negative to 4 in an ideal situation. This involves running three 2m cables (to connect 2 and 3 and a negative wire from 4 to the electronics). (Option A)
I could potentially wire them such that 1 connects to 3, 3 to 4, and 4 to 2. This would involve using four 2m cables (two from 1 to 3, two from 4 to 2). This would then allow me to use a short negative cable from 2. (Option B)
The question then, is what these distances/layouts do to voltage drop and wire thickness consideration? To try to ask for some specifics rather than leave it that wide...
1) When considering the 'circuit distance' from battery to inverter (etc) back to battery, what consideration is given to the wiring between batteries/cells in a parallel setup?
2) In Option A, assuming 25cm from Battery 1 to an inverter, and 2m from Battery 4 to the inverter, the total distance is either 2.25m or 4.25m or 6.25m depending on the answer to 1. In Option B, assuming the same 25cm from Battery 1 and 25cm from Battery 2, the total distance is either 0.5m, 4.5m or 8.5m. Which is it?
3) Is there a better way to wire this? :lol:
Many thanks in advance for any help anyone can offer!