Interesting Article on Fuses

deardancer3

10 kW
Joined
Dec 9, 2007
Messages
959
Location
San Diego
http://www.bcae1.com/fuses.htm


excerpt:
Suggested Fuse Sizes:

Wire Gauge Recommended
Maximum Fuse Size
00 awg 400 amps
0 awg 325 amps
1 awg 250 amps
2 awg 200 amps
4 awg 125 amps
6 awg 80 amps
8 awg 50 amps
10 awg 30 amps
12 awg 20 amps
14 awg 15 amps
16 awg 7.5 amps
These are the recommended maximum fuse ratings for the corresponding wire size. Using a smaller fuse than what's recommended here will be perfectly safe.




--------------------------------------------------------------------------------

Fuse Opening Time:
A fuse does not blow when the current reaches its rated current. It is designed to pass its rated current without opening. A fuse will take varying times to blow under different conditions. A fuse will pass significantly more than its rated current for a very short time. It may take 10 minutes or more to blow a fuse at 25% over its rated current. The table below is an example of the specifications for a slow blow fuse. You can see that a 20 amp fuse may pass 40 amps of current for as long as 5 minutes before blowing although it probably wouldn't take a full 5 minutes to blow. The times for other fuses will be slightly different.

%of amp rating Opening time
110% 4 hours minimum
135% 1 hour maximum
200% 5 minutes maximum
 