I know a bit of electrical house wiring, but not enough to be *certain* that I can safely do what I am asking about here. So before I destroy equipment or fry myself, I'd appreciate feedback from those familiar with and experienced in such things.
My house has regular split-phase 220VAC service at the box, with most of the house wired as 110VAC on one phase or the other. Two accesible points in the house are wired to the 220VAC across the phases, with a NEMA 10-30 receptacle, as HHN (Hot-Hot-Neutral). One is for a clothes dryer, and the other is for the kitchen stove/oven, both on 40A/phase breakers. The air conditioner is also on there, on separate 50A/phase breakers, but there is no accessible receptacle; it's direct wired.
The Sorenson DCS 55-55 lab supply I've got on loan has a NEMA L-6 plug on it, wired as HHG (Hot-Hot-Ground). It only needs 14A input with three phase, but with single phase like I have it'll take 20A (at max DC output, limited to ~2500W).
Given that it is unlikely any conductor will break to cause a shock hazard, using the spare cord off a dryer I have here, is it safe for the equipment to wire from the NEMA 10-30 as Y-W-X to the NEMA L-6 as Y-G-X? Meaning, tie Equipment Ground to House Neutral, as there is no separate ground available in the receptacle configuration I have?
I do realize that any internal equipment short by design or failure that allows neutral to short to case would then leave the case at whatever voltage Neutral is at, relative to ground, presenting a possibly fatal shock hazard; I'd be setting up the unit so contact with the case while attached to AC power is not easily possible even in my stupider moments (and impossible for the dogs to do so).
If it's not safe to do the way I describe, I'll have to find an install a NEMA L-6 receptacle, and wire it up.
This question is also posted at DIYEC, so I can confuse myself with as many opinions as possible.
My house has regular split-phase 220VAC service at the box, with most of the house wired as 110VAC on one phase or the other. Two accesible points in the house are wired to the 220VAC across the phases, with a NEMA 10-30 receptacle, as HHN (Hot-Hot-Neutral). One is for a clothes dryer, and the other is for the kitchen stove/oven, both on 40A/phase breakers. The air conditioner is also on there, on separate 50A/phase breakers, but there is no accessible receptacle; it's direct wired.
The Sorenson DCS 55-55 lab supply I've got on loan has a NEMA L-6 plug on it, wired as HHG (Hot-Hot-Ground). It only needs 14A input with three phase, but with single phase like I have it'll take 20A (at max DC output, limited to ~2500W).
Given that it is unlikely any conductor will break to cause a shock hazard, using the spare cord off a dryer I have here, is it safe for the equipment to wire from the NEMA 10-30 as Y-W-X to the NEMA L-6 as Y-G-X? Meaning, tie Equipment Ground to House Neutral, as there is no separate ground available in the receptacle configuration I have?
I do realize that any internal equipment short by design or failure that allows neutral to short to case would then leave the case at whatever voltage Neutral is at, relative to ground, presenting a possibly fatal shock hazard; I'd be setting up the unit so contact with the case while attached to AC power is not easily possible even in my stupider moments (and impossible for the dogs to do so).
If it's not safe to do the way I describe, I'll have to find an install a NEMA L-6 receptacle, and wire it up.
This question is also posted at DIYEC, so I can confuse myself with as many opinions as possible.