I have been part of the ebike community for over five years. I built two 16s4p battery packs using K-2 26650 energy cells (3.2v 3.2ah). The pack that’s causing today's problem was originally installed in the triangle of my back-up commuter ebike. The back-up ebike was in storage for approximately three months.
I need the great minds of this forum to assist me with the diagnosis and repair of a battery pack that I cannot charge using the BMS yellow wire (charger negative) and the pack red (positive). The BMS was purchased from Cell_man (Em3EV) over three years ago, along with a 48v 5ah charger.
I also use a Mastech 60v 20ah CC/CV power supply to charge the three ebikes in my stable. I cannot charge the battery through the BMS using the 48v charger or CC/CV. When I connect the charger, it immediately displays the green light. Same results when I attempt to charge the pack using the Mastech CC/CV through the BMS: there’s no current draw. The pack voltage does not increase using either charging source.
The identical 16s4p pack charges to 58.4 before the BMS shuts down the charger, or the Mastech power supply terminates the current. The cells of this pack were in service for months without a BMS as two 25.6v packs that I balanced every third charge cycle using an Imax8.
After purchasing the BMS from Cell_man, I chose not to remove the balancing wires from either of the two 25.6v packs before connecting them in series. This has allowed me to check the status of each cell with a Cellog8 without removing the all the duct tape.
My initial thought was a defective cell. I even purchase four replacement cells from Battery-Space in Richmond, however after checking each using the Cellog8 and my DMM, here are the cell voltages for the total pack, after a discharge of each 8s block using my Imax8:
1. 3.323
2. 3.331
3. 3.229
4. 3.329
5. 3.327
6. 3.329
7. 3.344
8. 3.339
9. 3.324
10. 3.327
11. 3.330
12. 3.340
13. 3.342
14. 3.336
15. 3.347
16. 3.339
When bypass the BMS, and charge the pack through the balance wires, the result is a healthy 58v, but without the BMS, a few of the cells were over 3.8v (3.65v is safe) until the bleed down using the Imax 8.
Shorts? Well, the negative (yellow) charging wire of the BMS continues to provide the SOC for the DMM and Cycle Analyst. Is it time to remove the duct tape from the pack and inspect the BMS? Thanks
I need the great minds of this forum to assist me with the diagnosis and repair of a battery pack that I cannot charge using the BMS yellow wire (charger negative) and the pack red (positive). The BMS was purchased from Cell_man (Em3EV) over three years ago, along with a 48v 5ah charger.
I also use a Mastech 60v 20ah CC/CV power supply to charge the three ebikes in my stable. I cannot charge the battery through the BMS using the 48v charger or CC/CV. When I connect the charger, it immediately displays the green light. Same results when I attempt to charge the pack using the Mastech CC/CV through the BMS: there’s no current draw. The pack voltage does not increase using either charging source.
The identical 16s4p pack charges to 58.4 before the BMS shuts down the charger, or the Mastech power supply terminates the current. The cells of this pack were in service for months without a BMS as two 25.6v packs that I balanced every third charge cycle using an Imax8.
After purchasing the BMS from Cell_man, I chose not to remove the balancing wires from either of the two 25.6v packs before connecting them in series. This has allowed me to check the status of each cell with a Cellog8 without removing the all the duct tape.
My initial thought was a defective cell. I even purchase four replacement cells from Battery-Space in Richmond, however after checking each using the Cellog8 and my DMM, here are the cell voltages for the total pack, after a discharge of each 8s block using my Imax8:
1. 3.323
2. 3.331
3. 3.229
4. 3.329
5. 3.327
6. 3.329
7. 3.344
8. 3.339
9. 3.324
10. 3.327
11. 3.330
12. 3.340
13. 3.342
14. 3.336
15. 3.347
16. 3.339
When bypass the BMS, and charge the pack through the balance wires, the result is a healthy 58v, but without the BMS, a few of the cells were over 3.8v (3.65v is safe) until the bleed down using the Imax 8.
Shorts? Well, the negative (yellow) charging wire of the BMS continues to provide the SOC for the DMM and Cycle Analyst. Is it time to remove the duct tape from the pack and inspect the BMS? Thanks