Inverter Huawei I23002G1 / I23003G1 - Embedded Telecom Power (ETP) - 48V 42~58V 3000w

Hyperelectronic

100 µW
Joined
Sep 29, 2024
Messages
7
Location
Austria
Hello all of you,

Short introduction from my side, I am an electrical engineer / electronics developer / firmware programmer from Austria who likes to deal with all kind of electrical components / electronics / battery storage systems ranging from very small power levels (uCs) up to very large ones (EVs). I also over the years have gained a lot of experience in the field of reverse engineering.

Currently I am working on reverse engineering the "Embedded Telecom Power" (ETP) modules from Huawei to get them working standalone and I already managed to get the rectifier modules fully working (complete remote control, status communication, diagnostic data (including fan management) via can bus, etc.) and currently already use them to charge my powerwall with the excess power of my solar system (3x R4875G1 modules connected to 3 phase ac power and managed by a central ESP32 board with fully automated load management / power control). Additionally I also have the super high efficiency variant of this modules (R4850S1) for testing purposes.

I am now working specifically on the inverter type of modules but simply can not get them to work so far. I tried measuring and manipulating all possible data signals on the connector, but can not get it to communicate via can bus and therefore can not control it / enable the output.
I already found out, that this kind of module seems to do not have the auto addressing functionality that the rectifier modules have and therefore need static addressing (set via resistors, which I could not exactly determine because I do not have an original enclosure for it, but by a bit of trial and error found a combination where the module does not simply signal an slot error but still no communication is possible)
The main problem is, that there is zero communication comming from the module (as there is with the rectifier modules), also sending a lot of different messages to it made no difference, I even tried to brute force it, but with 29 bit of possible addresses and a nearly infinite amount of possible data combinations, there is really no big chance to get it working this way. I tried the northbound and southbound can bus at different states at the other pins, I am also 100% sure the whole communication chain is working properly, as if i plug a rectfier module into the same connector everything is working perfectly and with both types of modules only at the correct 125 kbit/s there is no immediate can bus error if I send messages to it.

The last thing I did is let the GPT do a deep resarch but that also did not result in anything useful. The only reference I got are some videos of a guy (on a chinese video platform) that seem to be a engineer at huawei and he has posted some short videos on the module working externally (from the comments it seems to be very likely that it was done with some special firmware on it).

I believe there must be some kind of unlocking sequence build into it (I am not sure if it is implemented in hardware via pins or software via can bus) or if it is only to protect people from mains output voltage or to lock us out from using it externally.
So the only way and hope I have, is you guys, as I am currently quite stuck.
Does anyone of you have an ETP23003 or ETP23006 enclosure and can reach out to me, so we can do a few measurements? (I think we will be able to get it working in a very short time)

I also have a lot more detailed informations / measurement values and images of the electronics of the modules that I could / will provide if needed, but as I am always very bussy, I do not have a lot of time for documenting it online in detail.

Thanks a lot to all of you in advance!
 
I don't have experience with these, but there is significant discussion about telecom PSU repurposing here. If you haven't already you might look at the other here (mostly in the battery technology section) to see if any of the stuff done on those applies to yours. This is perhaps the biggest:
 
I don't have experience with these, but there is significant discussion about telecom PSU repurposing here. If you haven't already you might look at the other here (mostly in the battery technology section) to see if any of the stuff done on those applies to yours. This is perhaps the biggest:
Thanks for your comment, i really appreciate it, this is quite a good thread as there are also a lot of pictures posted, but I already knew it (I have even read it multiple times already) and I believe also nearly everything I could find anywhere about it.
 
I would also be very interested in any information about getting this inverter working outside the enclosure. I have the I23003G1, and naively assumed it would just start pumping out CAN messages like R4850/4875. I haven't done any testing yet, other than power it on connected to CAN...

By slot error, do you mean all three LEDs lighting up? If so, what did you do to solve that? And do you get any AC output at this point?

I assumed the unit needed some kind of AC signal to sync to, and maybe that was the problem based on the presence of "Parallel signal" pins: I23003G1 Inverter Module User Manual V1.0 | PDF | Power Inverter | Power Supply
 
I originally had expected the same and before I bought it, I was quite sure, that it would behave exactly the same as the rectifier modules do, which unfortunately seems to be everything else than true.

Correct, if nothing is connected to address pins 1 or 2, all three leds are lit (the red led is signaling an slot detect / address error), even if the pskill pin is connected to dc- to signal a fully plugged-in module, but this connection at least half way starts the module (it's starting the conversion from input voltage to the dc bus voltage (internaly measured at around 396 VDC) (only pulsating because no power gets drawn and therefore no discharge of dc bus except the bleeder resistors) but no communication via can bus and also no output is present).
If you additionally connect address pin 1 to dc- and address pin 2 to an external supply of greater than 2.2 VDC (for my testing I keept at 2.8 VDC but tried ranges up to arround 25 VDC as I have found some loose informations on a chinese forum, that on the ETP48xxx enclosures the range for the reference circuit might go up to arround half the dc input (not sure if it is true, but there really should not be any harm to it, even if it is way to high, because the module is compliant with international emc standard (with which I am very familiar with) and therefore gets tested with such and even higher levels on any exposed pins at certification) and then supply the module with power the red fault indicator led stays off (only the yellow and green leds are on) but still no communication or output.

From what I have found out so far, I am also not expecting that any of the sync signals need to be present for a single module to work (this section is also separated on the user manual), but I also have already tried hooking up a lot of different signals onto the parallel signal pins, unfortunately with no luck or change in behaviour.

I am really wondering if there must be a special signal / communication present on the DIO+ and DIO- pins to unlock the module.
 
For everyone that is curious, some informations specified in the original user manuals of the module and enclosure:

1.) Pinout of the I23003G1 inverter module

2.) Description of the dip switches that set the levels of the address pins 1 and 2
I believe they are directly (with some simple ciruit) connected to the 2 individual address pins on the module (so first group address pin 1 and second group address pin 2) but can not verify it as I do not have an enclosure for it.
But from my understanding, it would make sense why it is indicating an error without a connection of the second address pin, because it would maybe think it is in slave mode and therefore needs the parallel signals, which are not present.
 

Attachments

  • 1748071062254.png
    1748071062254.png
    68 KB · Views: 11
  • 1748071249593.png
    1748071249593.png
    55.5 KB · Views: 10
I don't have experience with these, but there is significant discussion about telecom PSU repurposing here. If you haven't already you might look at the other here (mostly in the battery technology section) to see if any of the stuff done on those applies to yours. This is perhaps the biggest:
,here is the video of controller
 
Hello all of you,

Short introduction from my side, I am an electrical engineer / electronics developer / firmware programmer from Austria who likes to deal with all kind of electrical components / electronics / battery storage systems ranging from very small power levels (uCs) up to very large ones (EVs). I also over the years have gained a lot of experience in the field of reverse engineering.

Currently I am working on reverse engineering the "Embedded Telecom Power" (ETP) modules from Huawei to get them working standalone and I already managed to get the rectifier modules fully working (complete remote control, status communication, diagnostic data (including fan management) via can bus, etc.) and currently already use them to charge my powerwall with the excess power of my solar system (3x R4875G1 modules connected to 3 phase ac power and managed by a central ESP32 board with fully automated load management / power control). Additionally I also have the super high efficiency variant of this modules (R4850S1) for testing purposes.

I am now working specifically on the inverter type of modules but simply can not get them to work so far. I tried measuring and manipulating all possible data signals on the connector, but can not get it to communicate via can bus and therefore can not control it / enable the output.
I already found out, that this kind of module seems to do not have the auto addressing functionality that the rectifier modules have and therefore need static addressing (set via resistors, which I could not exactly determine because I do not have an original enclosure for it, but by a bit of trial and error found a combination where the module does not simply signal an slot error but still no communication is possible)
The main problem is, that there is zero communication comming from the module (as there is with the rectifier modules), also sending a lot of different messages to it made no difference, I even tried to brute force it, but with 29 bit of possible addresses and a nearly infinite amount of possible data combinations, there is really no big chance to get it working this way. I tried the northbound and southbound can bus at different states at the other pins, I am also 100% sure the whole communication chain is working properly, as if i plug a rectfier module into the same connector everything is working perfectly and with both types of modules only at the correct 125 kbit/s there is no immediate can bus error if I send messages to it.

The last thing I did is let the GPT do a deep resarch but that also did not result in anything useful. The only reference I got are some videos of a guy (on a chinese video platform) that seem to be a engineer at huawei and he has posted some short videos on the module working externally (from the comments it seems to be very likely that it was done with some special firmware on it).

I believe there must be some kind of unlocking sequence build into it (I am not sure if it is implemented in hardware via pins or software via can bus) or if it is only to protect people from mains output voltage or to lock us out from using it externally.
So the only way and hope I have, is you guys, as I am currently quite stuck.
Does anyone of you have an ETP23003 or ETP23006 enclosure and can reach out to me, so we can do a few measurements? (I think we will be able to get it working in a very short time)

I also have a lot more detailed informations / measurement values and images of the electronics of the modules that I could / will provide if needed, but as I am always very bussy, I do not have a lot of time for documenting it online in detail.

Thanks a lot to all of you in advance!
try this one
 
I would also be very interested in any information about getting this inverter working outside the enclosure. I have the I23003G1, and naively assumed it would just start pumping out CAN messages like R4850/4875. I haven't done any testing yet, other than power it on connected to CAN...

By slot error, do you mean all three LEDs lighting up? If so, what did you do to solve that? And do you get any AC output at this point?

I assumed the unit needed some kind of AC signal to sync to, and maybe that was the problem based on the presence of "Parallel signal" pins: I23003G1 Inverter Module User Manual V1.0 | PDF | Power Inverter | Power Supply
Hello interested people,

very good news for you, I managed to get the I23003G1 module finally working, also nearly finished the reverse engineering of the full can communication protocol for it.

1a.jpg

Next steps on my list are getting these modules working in parallel and furthermore, even in a 3-phase configuration (120° phase shift) to finally power my full home with them and maybe even do some phase sync and try to feed into the grid (I am not fully sure, if this is even possible with the default module firmware, as currently I found no fine adjustment for voltage and dynamic fine adjustment for frequency, just the "type" by enum values (but this gets executed very precisely, so there is definitely quite some high potential).

Currently I am very busy and also this project by now is also by far one of the most expensive reverse engineering projects I have ever done. Currently I have already bought equipment for nearly $1500 for it, so if anybody would really like to get some "crazy" projects like these going and could afford to support me with just some small amount, it would really help me a lot. As I am actually no "coffee person", everything would be directly spent on new equipment ;) My support link: https://ko-fi.com/hyperelectronic

For now, stay tuned, I will definitely post updates / a full guide after I finished documentation or maybe even record some videos, if time allows for it!
 
Ohh, nice work! This is definitely exciting as I had kind of given up on this inverter myself.

Even just getting it working in single-phase and with a few CAN "statistics" would be enough for me.

Looking forward to the guide!
 
Status update: Quite a lot of progress during the last months (even though i was quite busy with other stuff), by now got 3 modules and managed to build a working cluster with them so that I can continue testing and finish my protocol definition.

You can see a short video of the current state at:
⚡Huawei I23003G1 Inverter Module - Standalone Operation
(Unfortunately not ac phase synced yet)

I hope I have some spare time in the next weeks to do further testing and therefore can share more information with you, until then stay tuned ;)
 